Correct? even the neutral in 120/240 could be gray?
I'm thinking, that BrnOrgYelGry and BlkRedBluWht would only be observed when these different voltages are present at the same point. (in a box or conduit)??
The NEC restricts the use of the following colorsYup, NEC does not mention color. Only when 2 voltages exist in a building they somehow be identified.
The NEC restricts the use of the following colors
White 200.6
Gray 200.6
Green 250.119
Orange 250.36
Light blue 504.80
Orange with a stripe 517.82 (5)
Brown with a stripe 517.82 (5)
The NEC used to have a color code requirement but it was removed in about the 1976 version.
I assume that you wanted to say 230.56 for the reference to the use of orange, but that rule and the other rules that suggest the use of orange to identify the high leg of a 4 wire delta system do not limit the use of the color orange for other applications.The NEC restricts the use of the following colors
White 200.6
Gray 200.6
Green 250.119
Orange 250.36
Light blue 504.80
Orange with a stripe 517.82 (5)
Brown with a stripe 517.82 (5)
The NEC used to have a color code requirement but it was removed in about the 1976 version.
Any idea why that section exists in 230 when 110.15 pretty much covers it anyway?I assume that you wanted to say 230.56 for the reference to the use of orange, but that rule and the other rules that suggest the use of orange to identify the high leg of a 4 wire delta system do not limit the use of the color orange for other applications.
The NEC restricts the use of the following colors
White 200.6
Gray 200.6
Green 250.119
Orange 250.36
Light blue 504.80
Orange with a stripe 517.82 (5)
Brown with a stripe 517.82 (5)
The NEC used to have a color code requirement but it was removed in about the 1976 version.
I assume that you wanted to say 230.56 for the reference to the use of orange,