A 3-phase, 460 volt wye pump service with no neutral loadrequires:

(a) a grounded service conductor be run to and isolated from the service disconnecting means.
(b) a grounding electrode conductor connected to the service disconnecting means.
(c) a grounded service conductor be run to and bonded to the service disconnecting means.
(d) no additional grounding or bonding.

Thanks....!:confused:
 
thanks Roger!

thanks Roger!

Roger, I appreciate the quick response. This is the only answer I didn't consider. Looks right to me after rereading it.
I'll take your word and thanks again !
John...
 

rm1212

Member
just to make sure

just to make sure

i have read over 250.24c and was wondering if the answer is (a grounded service conductor to be run to and bonded to the service disconnecting means) or am i still misunderstanding this?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
rm1212 said:
i have read over 250.24c and was wondering if the answer is (a grounded service conductor to be run to and bonded to the service disconnecting means) or am i still misunderstanding this?

That is the correct answer.

Roger
 