- Massachusetts
Re: Combination MC connectors
1996 NEC
[ January 08, 2006, 05:12 AM: Message edited by: iwire ]
I suggest you read the section again and and this time be sure to read Exception 8Originally posted by morepower:
This project is being built per the '96 NEC. 300-15(b)of the '96 NEC is clear:"...A box shall be installed at the connection point between any such cable system and a raceway system..."
1996 NEC
This is a common and accepted practice in the area I work, I have never seen conductors damaged by this method.310.15(b)Exception 8 A fitting identified for the use shall be permitted in lieu of a box where the conductors are not spliced or terminated.