What the title says.
I am replacing inverters on a legacy system.
New inverters are Sunny Tripower X-30-US with 3 MPPTs each.
The negatives for 3 strings are combined at the array into a single #8 AWG PV wire comig to the INV...........while (most of) the positives are individual (#10 AWG) for each string.
Can I wire 2 positives to one MPPT and the third to another MPPT, while "splitting" the common negative across both MPPTs?
(wire single common negative to both MPPTs with MC branch circuit "Y" connector AKA splitter or jumper)
I know this can be done with paralleled source circuits, but not sure about MPPTs.
OPTION 2:
More details:
Panel Imp is 8.68A (3 strings at 8.68 A = 26 A combined)
INV MPPT max DC input of 24 A operating.
So I guess I could wire it to a single MPPT but because there is ony on other neagtive lead.......I would only use 2 of 3 MPPTs on the INV. Not sure if that is a huge waste or none at all?
I am replacing inverters on a legacy system.
New inverters are Sunny Tripower X-30-US with 3 MPPTs each.
The negatives for 3 strings are combined at the array into a single #8 AWG PV wire comig to the INV...........while (most of) the positives are individual (#10 AWG) for each string.
Can I wire 2 positives to one MPPT and the third to another MPPT, while "splitting" the common negative across both MPPTs?
(wire single common negative to both MPPTs with MC branch circuit "Y" connector AKA splitter or jumper)
I know this can be done with paralleled source circuits, but not sure about MPPTs.
OPTION 2:
More details:
Panel Imp is 8.68A (3 strings at 8.68 A = 26 A combined)
INV MPPT max DC input of 24 A operating.
So I guess I could wire it to a single MPPT but because there is ony on other neagtive lead.......I would only use 2 of 3 MPPTs on the INV. Not sure if that is a huge waste or none at all?