I am told that a given transformer bank has (3) single phase 15kVA transformers connected in a wye-wye 3-phase transformer bank. I am told that each 15kVA single phase transformer has a %Z impedance of 1.2 and an X/R ratio of aproximately 1.1.
I'm pretty sure I know the answer but wanted to confrim when when modeling this arrangement for fault contribution it would be the same as modeling a 45kVA 3-phase transformer with a 1.2% impedance and 1.1 X/R ratio. Is this correct?
Also on a slightly different note why do utility transformers have such a low impedance value? In this case it is 1.2% but I have seen other larger transformers that also have a low %impedance compared to other distribution transofmers of the same size that typically have 5% impedance or there about. Is it simply because there will be less losses across the transofmer that the utility will have to pay for?
I'm pretty sure I know the answer but wanted to confrim when when modeling this arrangement for fault contribution it would be the same as modeling a 45kVA 3-phase transformer with a 1.2% impedance and 1.1 X/R ratio. Is this correct?
Also on a slightly different note why do utility transformers have such a low impedance value? In this case it is 1.2% but I have seen other larger transformers that also have a low %impedance compared to other distribution transofmers of the same size that typically have 5% impedance or there about. Is it simply because there will be less losses across the transofmer that the utility will have to pay for?