Combiner
rattus
How many of you have heard of a combiner? Just saw a video of some DIY guy making one, and he didn't seem to reallize that he had to have a split phase service to make it work. If you are going to go to this much trouble, why not just install a 240V breaker and outlet?
hbiss
EC, Westchester, New York NEC: 2014
Hawthorne, New York NEC: 2014
EC
You mean like a "Y" cord that plugs into two 120V receptacles, each on different phases, with a 240 cord cap on the other end? Whatever floats your boat I guess.
-Hal
GoldDigger
Placerville, CA, USA
Retired PV System Designer
-Hal
More like "Whatever sinks your boat"?
Any regulatory issues aside, if you connect a 240 volt load to such a combiner and unplug one of the two male connectors the exposed prongs will have 120V between hot and neutral, coming from the other receptacle.
Not all that different from hooking up a generator with a suicide cord,,,,
I believe some of the commercial units for that (not listed ?) use two relays in the junction box to prevent that exposure. Neither side is connected to the load unless both sides are energized.
jaggedben
Northern California
Combiner to me means where I bring together multiple solar sources, usually DC but could be used for AC as well.
I have no idea what you are talking about. :p
SceneryDriver
NJ
Electrical and Automation Designer
I had to build one of these things years ago to power a piece of 208V single phase equipment for a trade show booth. The venue would supply as many 120V circuit as you wanted, but if you requested a 208V receptacle of any type, they had to "bring in their electrician" to hook up power, which meant plugging into the spider box already present with a twist lock cable. The venue wanted something like $5k to do this.
I built the box in my hotel room, out of parts we bought at a local supply house and we hid it under a table in the trade show booth so the venue goons wouldn't see it. It had a pair of relays that prevented the male connectors from being energized if only one side was plugged in. It worked a treat, and I think I still have it somewhere in my garage.
SceneryDriver
Jraef
Electrical Engineer
I agree, I’ve only heard that term used in the solar industry to refer to the box where all of the panels are connected together. You need to define what you are referring to better.
ggunn
Austin, TX, USA
Electrical Engineer - Photovoltaic Systems
My take on it is that he wants to make a single 240V connection from two 120V outlets on different legs.
Small point - in solar there are DC and AC combiners. DC combiners connect the outputs of module strings in parallel and AC combiners connect the outputs of inverters (or sometimes groups of inverters) in parallel.
