Combining (4) single ended LV Switchgear to M-T-M-T-M-T-M lineup

Status
Not open for further replies.

philly

Senior Member
This question is for the same project I asked in my other post about HRG with multiple soures but question is of a different topic.

Customer wants to combine (4) individual sections of single ended MLO switchgear into a M-T-M-T-M-T-M arrangement by adding (4) tie breakers between each of the buses. These switchgear sections are currenly MLO and each from via a separate transformer from an upstream MV feeder breaker on a single ended switchgear lineup.

The idea would be to add main breakers to each lineup and interlock the tie breakers such that no more than two ties would be permitted to be closed at the same time.

Has anyone ever seen anything like this before. This seems like it provides a great bit of secondary selective reliability but is there a better way to accomplish the same reliability?
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Seen it in some medium voltage utility design where over 50MVA of load is involved- have also seen it in 4160 and 480 volt power plant drawings if memory serves right. It certainly is doable, but the question is, is it worth it for your application?
 

publicgood

Senior Member
Location
WI, USA
You note these are currently MLO sections via separate transformers. Are these wye secondary transformers? How is secondary protection of the feeders from the individual transformers to the MLO sections provided?

Only two ties may be closed at a time: does this mean transformers will be paralleled?
 