. Isnt a load calc and amp probe reading?I would RFI and find out what it is they expect. I would also want to do a load calculation on each existing branch circuit.
Amprobe is the brand name of a company that makes measurement equipment. You can't take ampere readings after you disconnect the circuit breaker. So my interpretation is that you are being asked to verify which circuit supplies power to which loads.
It appears to me that they are asking you to get the load current for each circuit and consolidate circuits to free up panel space. The issue with that is that you are only getting "snapshot" load information and would not really be a suitable method of determining if circuits could be consolidated unless steps were take to ensure that all possible loads were on at the time of the "snapshot" current reading.
So when you say "free up" panel space you mean have some spare breakers? Can you provide a little more detail as to why you're only getting a snapshot? Thanks
Go to my house on a Sunday afternoon and mesure the amp load on my bathroom recept circuits and you'll get nothing. Measure on a Friday afternoon when my daughter is getting ready to go out and the same circuits will be at max load because of all the curling irons running.
. Isnt a load calc and amp probe reading?
Load calc is a calculation that considers equipment ratings and may include demand factors - though demand factors usually apply to service or feeders more so then branch circuits.. Isnt a load calc and amp probe reading?
It appears to me that they are asking you to get the load current for each circuit and consolidate circuits to free up panel space.
Not sure I quite understand what they mean or what would be involved when they say consolidate extg. branch circuits. So take multiple extg. circuits and make them one circuit based on amprobe readings. Thanks.
Need to do that task would be more understood with design build, but with design build you won't have plans and specifications to estimate off of. You might have original or as built to work with and use to help come up with new design.Was or is a walk through available, go to it.
Sounds like lazy do my work for me, what do the panel schedules show?
Like others said most of the circuits would already be maxed, you would need the old as-builts and guess/hope they are true or add lots of trouble shooting time to calculate loads, again their job, unless this is a design build.
Remove change add breakers what the heck is that? Can the panel hold the calculated load, right they were supposed to determine that.
Not too late to no bid!
I would rfi this big time, or move on to a better bid that won't end up in court, if you can find one!