combining electrical service for 3 suites
combining electrical service for 3 suites
Since NEC 230.71(A) permits 6 disconnects that are grouped together, I do not see a problem with this configuration just as long as plaques are installed indicating which 3 service switches service the combined suite.
As far as the electrical utility is concerned, there are 3 ways to totalize the 3 feeders. One of them is to use some current transformers, either 2 or 6 for single phase, and connect these to a form 5s, 45s, or General Electric form 9s Fitzall(TM) meter.
The other way is to use 3 General Electric KV2c or KV2c+ meters can be ganged together so that only 1 of them needs to be read. You would equip each meter with a type M i/o cord and equip each socket with a socket extender from Marwell with a 1 inch hub in the 6 o'clock position. 1 inch flexible liquidtight conduit would extend from there to a place to splice the wires together. Pulse output from 2 of the meter would be connected to the 3rd meter and this one would be the one that is read and would have time of use metering and so forth. I am not sure if meter 1 can be set to send pulses to meter 2 and meter 2 then sends subtotal pulses to meter 3 - I will have to ask Russ Grenier about this issue. Anyways, 1 way to terminate the #26 stranded wires is to use a Siemon multiflex type 66 punchblock to accept the wires.
Now if I were wiring this type of building and it were my building and lets say that load calculation amounts to 100 amps per suite single phase or 3 phase, I could install a 200 amp per position metering center and big enough conduits so that 1 panelboard can be upgraded to 200 amps and say a pair of 60 amp subfeeds run from there to the other 2 combinded suites. This would save a little hassle in the long run if this is an upscale building where some people want to combine 3 suites.
Mike Cole, mc5w at earthlink dot net