I have two 800A feeds ( 2 500kcmil/phase each feed)fed from two different breakers on the same substation. The 30 day maximum 15minute demand on these feeds is 250 on one and ~200 on the second. I am looking to change out the lugs on one of the breakers (to handle 4 500kcmil/phase) and feed these loads from one breaker to free up a breaker. Does this sort of load combining fall under 220.35? If it does from a calculation standpoint should both 30 day readings be multiplied by 1.25 and then added to verify total load per 220.35 (2)?