Thank you this is one of those situations where it just does not feel right. So assuming all ckts #12 one #12 jumper from wireway to panel would suffice. Or if paint is removed or ground bar is threaded properly no wire required and you could rely on conduit as EGC. I see where this could greatly reduce Panel traffic.Yes a single bonding jumper sized for the largest circuit is permitted. If the paint were removed behind the ground bar the jumper can be eliminated.
Either scenario would be code compliant.So assuming all ckts #12 one #12 jumper from wireway to panel would suffice. Or if paint is removed or ground bar is threaded properly no wire required and you could rely on conduit as EGC.
Thanks again I could not find anything to prohibit this but for some reason in my head it just felt wrongEither scenario would be code compliant.
It's unlikely that multiple circuits will short to ground at the same time.Thanks again I could not find anything to prohibit this but for some reason in my head it just felt wrong