C cppoly Senior Member Location New York May 21, 2013 #1 A refrigeration appliance has 4.1 amps with max OCPD 15 amps. Another appliance has 2.3 amps with no max OCPD. Can both of these go on one 15 amp circuit breaker?
A refrigeration appliance has 4.1 amps with max OCPD 15 amps. Another appliance has 2.3 amps with no max OCPD. Can both of these go on one 15 amp circuit breaker?
ActionDave Chief Moderator Staff member Location Durango, CO, 10 h 20 min from the winged horses. Occupation Licensed Electrician May 22, 2013 #2 Yes, but there is a chance the manufacture's instructions will call for a dedicated circuit.