Combustible Material within boxes

Status
Not open for further replies.

IBEW3NY

New User
Location
Connecticut
Occupation
Construction Electrician
Does anyone know if it’s a violation to mount plywood within any type of electrical boxes? I cannot find it in the NEC, but I may not be looking in the correct section. Any help would be appreciated..
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Inside of an electrical box should be fine unless it contains an arc producing device.

110.18 Arcing Parts. Parts of electrical equipment that in ordinary operation produce arcs, sparks, flames, or molten
metal shall be enclosed or separated and isolated from all combustible material.
 