Comercial 20amp minimum circuit requiered

Status
Not open for further replies.

jzadroga

Member
Location
MA
I recently had a discussion with the local electrical inspector and the subject of comercial branch circuits came up. The inspector said that 15 amp general use branch circuits are permitted in the NEC. Now I can't exactly remember when or where in the NEC, but I think that there is a requirement that general use branch circuits are required to be 20 amp circuits in comercial buildings. Can anyone support my uderstanding with the code section that applies??
 

joe tedesco

Senior Member
Re: Comercial 20amp minimum circuit requiered

600.5(A) ...... The outlet(s) shall be supplied by a branch circuit rated at least 20 amperes that supplies no other load........


This was the only place I could find where this sentence was used. See Articles 210 and 200 for calculations.
 

charlie

Senior Member
Location
Indianapolis
Re: Comercial 20amp minimum circuit requiered

Generally speaking, the transformer for a commercial service is much closer to the building and it is larger. Therefore, more fault current is available to damage conductors (and equipment). Many areas have passed rules similar to "#14 Copper conductors are not permitted for commercial or industrial applications." This is not generally an NEC requirement but a local one.

It is the responsibility of the project electrical designer to verify if #14 can be used because of acceptable voltage drop, the load on the circuit, the conductor damage curves, etc. Many times, #14 may be used but you will see a note on the prints or specifications that do not permit anything less than #12 for the branch circuits. :cool:
 