I was doing a plan review on a business shell the other day. The EE had a computed load of 748 Amps, ws using parrellel 500's and an 800A breaker. I reviewed the calculations and found that he/she had used 2VA per square foot instead of 3 for lighting. Once I re-figured the calculations, I came up with 790 amps. I included on my list that he would have to re-size his conductors to greater than 500's, but I couldn't write anything about the ACPD rating.
What is your comfort level? If you were designing this building (future provisions for 5 small mercantile tenants), would you keep the 800 OCPD, or would you increase it once your calculated load was within 10 amps of the rating of the switch?