What code section would you cite if someone came into the top of a 3r cabinet or wireway with RGS and standard locknuts?
What code section would you cite if someone came into the top of a 3r cabinet or wireway with RGS and standard locknuts?
What code section would you cite if someone came into the top of a 3r cabinet or wireway with RGS and standard locknuts?
For enclosures in wet locations,
raceways or cables entering above the level of uninsulated
live parts shall use fittings listed for wet locations
What code section would you cite if someone came into the top of a 3r cabinet or wireway with RGS and standard locknuts?
and as long as accumulated water can drain per 314.15 (hey, that's 100 pi!), I don't see the violation. Granted, I see it as an obvious bad practice, but I don't see a direct violation of the NEC.
conduit bodies, and fittings installed in wet locations shall
be listed for use in wet locations.
The last sentence of 314.15
conduit bodies, and fittings installed in wet locations shall
be listed for use in wet locations.
The last sentence of 314.15
Are lock nuts considered to be fittings, and if so, are there lock nuts listed for use in wet locations?
Fitting. An accessory such as a locknut, bushing, or other
part of a wiring system that is intended primarily to perform
a mechanical rather than an electrical function
But here we go, from article 100
Sealing locknut should be acceptable.Fitting. An accessory such as a locknut, bushing, or other
part of a wiring system that is intended primarily to perform
a mechanical rather than an electrical function
Thank you. I would have looked it up myself but I am busy taking advantage of the weather and doing some stuff outside.
So, that being said, are there locknuts listed for use in wet locations? Or would there have to be a hub or the like instead?
Sealing locknut should be acceptable.
As could be the case with OP's 3R enclosure as well.It may work, but is it listed for use in a wet location? All I see is they are raintight. Wet locations also include in direct contact with the earth, and other applications where raintight may not be suitable.
As could be the case with OP's 3R enclosure as well.
For enclosures in wet locations,
raceways or cables entering above the level of uninsulated
live parts shall use fittings listed for wet locations
Note that it does not say you have to use fittings listed for wet locations all the time. Only if the raceway comes in above the level of live parts. If there are no live parts wet area fittings are not required.
conduit bodies, and fittings installed in wet locations shall
be listed for use in wet locations.
Note that it does not say you have to use fittings listed for wet locations all the time. Only if the raceway comes in above the level of live parts. If there are no live parts wet area fittings are not required.
Ok so the proposal in the OP wouldn't be "a violation of the wireway" , it would be a "violation of the fitting." So to expand on the topic, what would you cite for installing a nema1 wireway outdoors? 110.3?
376.10 Uses Permitted. The use of metal wireways shall
be permitted as follows:
(3) In wet locations where wireways are listed for the
purpose.
For a wireway