This is truly a unique situation that has my head spinning. I am installing a contactor to 'override' the house lights in a bar/ restauarant, so when the fire alarm system is activated, the lights jump to full illumination, and the sound (televisions, juke box, stereo, etc) shut down. The problem is that the work area is so limited and tight (it has 2 separate main panels, one to the far left, one to the far right, and a subpanel in between being fed from the panel on the left) that my ONLY option is to install the contactor about 2" below a horizontal trough used as a wire way for service entrance cable, and to move circuits from the far right panel to the middle panel (these are for receptacles and will be shut down using a shunt trip breaker at the main panel, the one on the left) and circuits from the middle panel to the far right panel ( these are lighting circuits that will go through the contactor). I have NO alternative but to use the panels as 'raceways' and splice the circuits I am moving onto THHN, run through emt for one panel to the next. So a circuit in the far right panel is removed from a breaker, and spliced onto THHN, through emt pipe into the middle panel and landed on a breaker there, The neutrals are moved as well. The same goes for moving the circuits from the middle panel to the far right. IS THIS LEGAL ????????