Commecial partition office furnishings box access

This issue has come up again. Even though is do like having the j box for the cubicle furnishings easy accessible without taking apart part of the partition, it was shown to me that technically it's not a code violation to block them because the partitions are not part of the 'building structure's or finish.'

Now a different inspector has started tagging it and saying it is a violation recently on projects.

Has the enforcement changed in any one else's area? Are they calling out the cubicle furniture as violations when they block the connection j box?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Has the enforcement changed in any one else's area? Are they calling out the cubicle furniture as violations when they block the connection j box?
The junction box has to be accessible. IMO a furniture partition is not part of the building structure or finish so having to remove a section to access the box is not a violation.
 