I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 0-0 210.19(B)(2)(2). Thanks, Jim Williams
4 Comment:
210.19 Conductors ? Minimum Ampacity and Size.
(B) Branch Circuits Over 600 Volts.
(2) Supervised Installations.
(2) Qualified persons with documented training and experience in over 600-volt systems provide maintenance, monitoring, and servicing of the system.
5 Statement of Problem and Substantiation.
Is 210.19(B)(2)(2) still needed now that we have spread 1000V over the majority of the NEC?