fmtjfw
- Fairmont, WV, USA
I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 1-130. Thanks, Jim Williams
4 Comment:
Revise text to read as follows:
110.25 Lockable Disconnecting Means. Where a disconnecting means is required to be lockable open, elsewhere in this Code, it shall be capable of being locked in the open position. T the provisions for locking shall remain in place with or without the lock installed.
red indicated deleted text
5 Statement of Problem and Substantiation:
The deleted phrase is redundant and adds nothing to the section. Requiring something to be capable of meeting the requirement is overkill.
4 Comment: