I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 15-41. Thanks, Jim Williams
4 Comment:
red -- delete
517.19 Critical Care Areas.
(C) Operating Room Receptacles
(2) Receptacle Requirements. The receptacles required in 517.19(C)(1) shall be permitted to be of the single, or duplex or quadruplex types or any combination of both.
5 Statement of Problem and Substantiation.
Hospital grade quad receptacles are available. They are referenced in other receptacle descriptions in 517.
4 Comment:
red -- delete
517.19 Critical Care Areas.
(C) Operating Room Receptacles
(2) Receptacle Requirements. The receptacles required in 517.19(C)(1) shall be permitted to be of the single, or duplex or quadruplex types or any combination of both.
5 Statement of Problem and Substantiation.
Hospital grade quad receptacles are available. They are referenced in other receptacle descriptions in 517.