fmtjfw
- Fairmont, WV, USA
I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 15-70. Thanks, Jim Williams
4 Comment:
517.32 Life Safety Branch.
(F) Generator Set Accessories. Generator set accessories as required for generator performance. Loads dedicated to a specific generator, including the fuel transfer pump(s), ventilation fans, electrically operated louvers, controls, cooling system, and other generator accessories essential for generator operation, shall be connected to the life safety branch or to the output terminals of the generator with over-current protective devices directly or through a transformer.
5 Statement of Problem and Substantiation.
In the case where the generator output voltage is not compatible with the listed loads is it acceptable for the load to be supplied from a transformer fed from the generator output leads?
4 Comment: