COMMENT 17-55 424.44(D)

Status
Not open for further replies.

fmtjfw

Senior Member
I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 17-55. Thanks, Jim Williams

4 Comment:
revise the text as follows:

red indicates deleted text

424.44 Installation of Cables in Concrete or Poured Masonry Floors.
(D) Spacing Between Heating Cable and Metal Embedded in the Floor. Spacing shall be maintained between the heating cable and metal embedded in the floor, unless the cable is a grounded metal-clad cable.has a grounded metal sheath.

5 Statement of Problem and Substantiation

It is unclear to me what is required to be grounded. If it is the sheath, then I suggest a change to the text. If something else is to be grounded, then perhaps other text is required.
 
Status
Not open for further replies.
Top