fmtjfw

Senior Member
I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 18-102a. Thanks, Jim Williams

4 Comment:

600.6 Disconnects.
(B) Control Switch Rating.
Switches, flashers, and similar devices controlling transformers and electronic power supplies shall be rated for controlling inductive loads or have a current rating not less than twice the current rating of the transformer or the electronic power supply. [ROP 18?102a]

5 Statement of Problem and Substantiation.

Transformerless electronic power supplies typically have high inrush currents.
 