COMMENT 18-38 422.51(A)
fmtjfw
I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 18-38. Thanks, Jim Williams
4 Comment:
revise text as follows:
422.51 Vending Machines.
(A) Cord- and Plug Connected. Cord-and-plug-connected vending machines manufactured or remanufactured on or after January 1, 2005, shall include a ground-fault circuit interrupter identified for portable use as an integral part of the attachment plug or be located within 300 mm (12 in.) of the attachment plug. Older vending machines manufactured or remanufactured prior to January 1, 2005, shall be connected to a GFCI-protected outlet. The GFCI protecting a vending machine shall meet the requirements of 110.26.
5 Statement of Problem and Substantiation.
Unlike portable pressure washers vending machines are often difficult to, so required the GFCI to be readily accessible is appropriate. Note another comment modified other text in 422.51(A), those changes are separate and not shown here.