COMMENT 19-43a 550.32(C) <info>

Status
Not open for further replies.

fmtjfw

Senior Member
I'm looking for constructive criticism on the following, and if you think it is merited, support in the form of comments from you on 19-43a_550.32C. Thanks, Jim Williams

4 Comment:

red means delete

550.32 Service Equipment.
( C) Rating.
Mobile home service equipment shall be rated at not less than 100 amperes at 120/240 volts, and provisions shall be made for connecting a mobile home feeder assembly by a permanent wiring method. Power outlets used as mobile home service equipment shall also be permitted to contain receptacles rated up to 50 amperes with appropriate overcurrent protection. Fifty-ampere receptacles shall conform to the configuration shown in Figure 550.10(C).

Informational Note: Complete details of the 50-ampere plug and receptacle configuration can be found in ANSI/NEMA WD 6-2002 (R2008), National Electrical Manufacturers Association, Standard for Wiring Devices ? Dimensional Requirements, Figure 14-50. [ROP 19?43a]

5 Statement of Problem and Substantiation.

The complete description of the receptacle is found in 550.10(C). The informational note is not necessary.
 