commercial 200 amp sizing

Status
Not open for further replies.

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
I do almost entirely residential, so it's been a while for commercial. For a commercial 200 amp service for a local auto mechanic, I'm planning on using (3) 250 AL service entrance conductors in a 2 " PVC riser, and the point of attachment is the building. (Saving some money instead of using 3/0 Cu) Is it ok to use pvc pipe between the meter and panel instead of metal conduit? (opposite each other on the concrete wall) EGC #4 Cu. One 5/8 ground rod or two? Indiana. Do these sound ok? He presently has an old 60 amp service. Thank you.
 

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
PVC is fine. 250 Al and 4Cu egc good. Two ground rods if that's all you have to choose from,,,,, no building steel present?
Thanks, I will check for building steel. He is adding on to an old concrete block wall and wood framed roof building, so there may not be any steel. I will try to ask the local inspector, too. I'm assuming I will also need to run a # 4 Cu to a water line and gas line (if there is one.) His furnace is a used motor oil type.
 

kwired

Electron manager
Location
NE Nebraska
4/0 aluminum can be protected by 200 amp breaker, but calculated load can not be more then 180 amps.

1/2 inch ground rod is acceptable if it is listed, unless you can prove the first rod has a resistance of 25 ohms or less you will need a second rod.

Gas line only needs bonded by the EGC of the circuit that may energize it. But if you happen to have CSST gas piping, that opens a can of worms for bonding requirements - and those are specific to the particular product being used more so then an across the board bonding requirement.
 