• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

Commercial 600 amp service

TYINMW

Member
Location
TEXAS
Occupation
ELECTRICAL CONTRACTOR
On a 600 amp 208 volt 3 phase underground service, is there a maximum distance allowed between secondary side of transsocket and exterior service disconnect?


TIA
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Is the transocket on the building? As long as the service conductors are on the outside of the building there is no limit to their length.
 
Top