wrobotronic Senior Member Location Colorado Sep 30, 2015 #1 Is there anywhere in the code that states a requirement for receptacles in commercial bathrooms? I only see requirements for dwellings. Thank you.
Is there anywhere in the code that states a requirement for receptacles in commercial bathrooms? I only see requirements for dwellings. Thank you.
iwire Moderator Staff member Location Massachusetts Sep 30, 2015 #2 wrobotronic said: Is there anywhere in the code that states a requirement for receptacles in commercial bathrooms? I only see requirements for dwellings. Thank you. Click to expand... No, not required.
wrobotronic said: Is there anywhere in the code that states a requirement for receptacles in commercial bathrooms? I only see requirements for dwellings. Thank you. Click to expand... No, not required.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Oct 1, 2015 #3 As Bob stated this is a design issue not a code issue. If you install them they can be on a 15 amp general purpose circuit.
As Bob stated this is a design issue not a code issue. If you install them they can be on a 15 amp general purpose circuit.
kwired Electron manager Location NE Nebraska Occupation EC Oct 1, 2015 #4 I will add GFCI protection is required on any receptacles that are installed, but there is no general requirement to install any.
I will add GFCI protection is required on any receptacles that are installed, but there is no general requirement to install any.