commercial building receptacles

Status
Not open for further replies.

dimlight

Member
Location
virginia
Occupation
electrician
I am replacing 3 prong receptacles in a commercial building that has metal conduit and metal boxes inside block walls. They were previously replaced with 3 prong receptacles with obviously no ground wire. I know the rules for residential as afar replacing ungrounded receptacles, but since the conduit was used as the EGC should I still use a GFI breaker/receptacle? Thanks
 
No you don't need a GFCI but you need to comply with 250.146

Roger
 
As long as the receptacles are self-grounding you can just screw them into the grounded metal box.
 