sparkybr549
I am new to this forum, and would appreciate any help. How many lumens/watts per sq.ft are required for stairwells in a commercial building. Are they considered as part of the minimum lighting requirements,
1006.2 Illumination level. The means of egress illumination
level shall not be less than 1 foot-candle (11 lux) at the walking
surface level.
Are you talking about normal usage, or during a power failure?raider1 said:This section comes from the 2006 IBC.
A stairway is part of the means of egress, so this section applys to stairways.1006.2 Illumination level. The means of egress illumination level shall not be less than 1 foot-candle (11 lux) at the walking surface level.
LarryFine said:Are you talking about normal usage, or during a power failure?
Interesting. Here in Richmond, they measure for a minimum of 1 ft-cdl at the floor for the entire egress pathway during power failure, not 0.1. Could they have been mis-inspecting all these years?raider1 said:The section that I quoted is for normal usage.
The section on emergency power requires that the inital emergency power illumination, for the means of egress be at least an average of 1 foot-candle and a minimum of 0.1 foot-candle measured along the path of egress at floor level.
LarryFine said:Interesting. Here in Richmond, they measure for a minimum of 1 ft-cdl at the floor for the entire egress pathway during power failure, not 0.1. Could they have been mis-inspecting all these years?
1006.4 Performance of system. Emergency lighting facilities
shall be arranged to provide initial illumination that is at least
an average of 1 foot-candle (11 lux) and a minimum at any
point of 0.1 foot-candle (1 lux) measured along the path of
egress at floor level. Illumination levels shall be permitted to
decline to 0.6 foot-candle (6 lux) average and a minimum at
any point of 0.06 foot-candle (0.6 lux) at the end of the emergency
lighting time duration. A maximum-to-minimum illumination
uniformity ratio of 40 to 1 shall not be exceeded.
I don't know what the local codes in your area are so this might be different. I would check with your local building department.
Chris
I'll double-check tomorrow.raider1 said:Are you under the IBC in Richmond?
sparkybr549 said:Thanks Cris for your information. This will help me forward to Supervisor, and is appreciated. Sparkybr549