J Jerry Kennedy New member Location Sacramento,CA Feb 14, 2012 #1 What is the required seperation of conductors in a 480 v 3 phase Solar Inverter. Ours appear to only have about an inch seperating the phases?
What is the required seperation of conductors in a 480 v 3 phase Solar Inverter. Ours appear to only have about an inch seperating the phases?
ron Senior Member Location New York, 40.7514,-73.9925 Feb 14, 2012 #2 Do you mean between insulated phase A, B and C or some other circuit of another voltage? If just A, B and C, then there is no minimum. They coexist in conduit touching each other.
Do you mean between insulated phase A, B and C or some other circuit of another voltage? If just A, B and C, then there is no minimum. They coexist in conduit touching each other.