Extensive corrosion to switch gear... it this generally an automatic replacement?

Also, service to switch gear from street - threaded connection just penetrates enclosure.

Any advice would be appreciated
 

Attachments

  • DSCF3351.jpg
    DSCF3351.jpg
    122.6 KB · Views: 1
  • DSCF3359.jpg
    DSCF3359.jpg
    128.2 KB · Views: 1
IMO you need to be careful when calling something "extensive corrosion", does the corrosion make the installation less safe or is just a cosmetic thing because it's old? Yes there should be locknuts on that raceway entering the enclosure.
 
IMO you need to be careful when calling something "extensive corrosion", does the corrosion make the installation less safe or is just a cosmetic thing because it's old? Yes there should be locknuts on that raceway entering the enclosure.

Yeah... that is my quandary... I was not going to open up the equipment (beyond my scope of assessment). Just gunna recommend client hire a licensed electrical contractor to perform detailed assessment inside.

Another photo attached... steel has thickened at the top from the corrosion process
 

Attachments

  • DSCF3363.jpg
    DSCF3363.jpg
    134.7 KB · Views: 0
Corrosion of the panel case isnt nearly as big a deal as corrosion of EGC lug, knife/fork mechanism, terminations, etc. Years ago I threw a 208V knife/fork non-fused disco for a 10 ton AC unit. When I removed the deadfront, I realize the center phase knife/fork had corroded together, and ripped loose the corroded lugs from the frame. Another 1/16th" and it would have thrown that conductor into the deadfront and probably blown up in my face.

Corrosion can also greatly increase resistance at terminations causing heat and fire. Yes, I would recommend an EC give the switch gear an inspection/evaluation.
 