commercial diner in home

Status
Not open for further replies.
New kitchen and emt for all that is new. Gray area seems to be existing plugs in home where now dining room. Not bx. Tearing out walls big amount of time and expense. Owner advised to contact inspections dept. Will the total home need rewire?
 
willywestinghouse said:
New kitchen and emt for all that is new. Gray area seems to be existing plugs in home where now dining room. Not bx. Tearing out walls big amount of time and expense. Owner advised to contact inspections dept. Will the total home need rewire?

Not all commercial buildings need to be wired with metallic raceways. Check and see what Type construction it is and read art. 334.10.


I would get a ruling from the local inspections department.
 
I did a remodel on a house to restaraunt several years ago. A very good chance the building is of a type V construction. Unless your local code is an issue, romex would be ok.
 