1 101010 Senior Member Mar 12, 2009 #1 Can you use a breaker lock on a commercial 40 amp 2pole dishwasher as disconnect?
B bphgravity Senior Member Location Florida Mar 12, 2009 #2 Yes. If you meet all the provisions of 422.31(B) of the NEC. Take a good look at Part III. Disconnecting Means of Article 422.
Yes. If you meet all the provisions of 422.31(B) of the NEC. Take a good look at Part III. Disconnecting Means of Article 422.