Commercial Dryer overcurrent protection

Merry Christmas
Status
Not open for further replies.

johnnyp

Member
I have three 3 phase 240 volt commercial dryers with name plate ratings of 79 amps. The name plates state that a 100 amp breaker is "recommended". The delima I have is that I have existing 125 amp circuits that I can use without making any changes. 422.10 requires a branch circuit "not less than" 125% for continuously loaded appliances. Since the name plate doesn't give me maximum size overcurrent device do you think I will be OK with the 125a breakers or should I change them to 100a breakers.
 
Re: Commercial Dryer overcurrent protection

why not use your 125 amp circuit and just fuse the disconnect at 100 amps.
 
Re: Commercial Dryer overcurrent protection

I would go with what the manufacturer recommends, sceepe's suggestion sounds good.
 
Re: Commercial Dryer overcurrent protection

Originally posted by sceepe:
why not use your 125 amp circuit and just fuse the disconnect at 100 amps.
if the instructions say to use a breaker would you not be at least technically in violation if you used a fuse?
 
Re: Commercial Dryer overcurrent protection

If no maximum OCP is specified, I'd leave well enough alone.
 
Re: Commercial Dryer overcurrent protection

Thanks guys. I think I will go with the manufacturers reccomendation to be safe. I appreciate the responses.

John
 
Re: Commercial Dryer overcurrent protection

Johnny, The rating of the dryer in questions sounds like an industrial dryer. It is not classified as an "Appliance" according to Article 100. I assume it is a listed by a testing laboratory, so the installation instructions must be followed as required by 110.3(B). If it is a listed product, the motor and heater loads are precalculated and the 79 amp rating includes the 125% required for the motor load in 430.22 and 430.24. Seems to me that the 100 amp breaker is the way to go.
 