I'm trying to determine if a feeder to a spa is of adequate size. The spa will provide services such as massage, sauna, steam, facials, nails and all that girly stuff. Figuring a feeder/panel size in a commercial space is new to me.
The spa has there own 100 amp 120/208 three phase panel from their own meter. I get 208*100*1.73 for a total of 36KW. The space is 2200 square feet.
The biggest loads are two steam units (8kw each), sauna(2800w), A/C(7200w), combo washer dryer, microwave, a couple of exaust fans that will pull steam out of the steam rooms, washer/dryer combo, DW, Water Heater and lighting.
When I plug in my estimates of the individual loads I get 43KW and that doesn't even address which loads are continuous.
If I assume all loads are continous I figure a 150 amp panel is required. In reality the steam units are not continous but at least I get a cushion. Am I doing this right?