Commercial garage load calcualtion

Status
Not open for further replies.

anbm

Senior Member
Location
TX
Occupation
Designer
For commercial garage with 60 repair bays, each bay has one auto lift machine (208V/1PH, 2HP, 14A),
should I size the electrical panel large enough to handle all 60 lift machines run at the same time?

I am looking at article 511 and don't see a demand factor to use for calculation. The owner said max. 15% of
these lift can operate at the same time? This is probably true, but I guess we have to stick to NEC to size the panel?
Any inputs on this?
 
Every one of those lifts I have ever seen has a duty cycle.

Then there is 430.26 - not any concrete requirements there but something to start with.

I bet you seldom ever see 15% of them running at same time. Most don't draw power when lowering, just a hydraulic release and let gravity do the work.

Many likely never see full motor nameplate amps either, even if lifting max lift rating.
 