I suspect this is simply a matter of personal preference. But I'd like to hear opinions or recommendations.
There is only one distribution panel for this space. There is a commercial hood that's fed control power from a 120V/15A dedicated branch circuit (12AWG conductors). The hood control package includes a two-terminal connection (hot and neutral) for tripping a shunt trip breaker; this is to de-energize all electrical equipment under the hood in the event of a fire. The shunt trip neutral terminal in the hood control package is simply jumpered from the incoming control power branch circuit neutral.
I could run two 14AWG conductors from these shunt trip terminals (hot and neutral) back to the shunt trip breaker. Or I could just run a single 14AWG conductor (hot) back to the breaker and connect the neutral from the breaker's shunt trip coil to the neutral bar in the distribution panel. Either way would allow the system to work as intended.
I contacted the hood manufacturer and asked for their recommendation and they said they've seen both methods used in installations.
On one hand, adding the dedicated neutral conductor does create a physical manifestation of the shunt trip loop circuit and it may appear more "professional." On the other hand, the hood is ~100 ft from the distribution panel, so installing a second shunt trip conductor just to carry neutral back to the distribution panel seems like a waste of copper. Plus, that means the round trip for the current is ~400 ft (as opposed to ~200 ft for jumpering the neutral in the distribution panel), although voltage drop won't be an issue either way since the shunt trip coil only draws 0.6A.
Which way would you wire this?
There is only one distribution panel for this space. There is a commercial hood that's fed control power from a 120V/15A dedicated branch circuit (12AWG conductors). The hood control package includes a two-terminal connection (hot and neutral) for tripping a shunt trip breaker; this is to de-energize all electrical equipment under the hood in the event of a fire. The shunt trip neutral terminal in the hood control package is simply jumpered from the incoming control power branch circuit neutral.
I could run two 14AWG conductors from these shunt trip terminals (hot and neutral) back to the shunt trip breaker. Or I could just run a single 14AWG conductor (hot) back to the breaker and connect the neutral from the breaker's shunt trip coil to the neutral bar in the distribution panel. Either way would allow the system to work as intended.
I contacted the hood manufacturer and asked for their recommendation and they said they've seen both methods used in installations.
On one hand, adding the dedicated neutral conductor does create a physical manifestation of the shunt trip loop circuit and it may appear more "professional." On the other hand, the hood is ~100 ft from the distribution panel, so installing a second shunt trip conductor just to carry neutral back to the distribution panel seems like a waste of copper. Plus, that means the round trip for the current is ~400 ft (as opposed to ~200 ft for jumpering the neutral in the distribution panel), although voltage drop won't be an issue either way since the shunt trip coil only draws 0.6A.
Which way would you wire this?