Commercial kitchen ceiling outlet

Merry Christmas

DudeElectric

Member
Location
Montana
I have a client that has a commercial kitchen and they would like to put a plate warmer in the center of their kitchen. It is on Wheels and is movable and the only Outlet is one in the ceiling approximately 10 ft. I can't for the life of me find out what the code is to get power from there too the plate warmer. Could somebody point me in the right direction? I'm fairly certain I can't just run conduit down as it wouldn't be secured at all. The plate warmer is just a 120 plug.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I have a client that has a commercial kitchen and they would like to put a plate warmer in the center of their kitchen. It is on Wheels and is movable and the only Outlet is one in the ceiling approximately 10 ft. I can't for the life of me find out what the code is to get power from there too the plate warmer. Could somebody point me in the right direction? I'm fairly certain I can't just run conduit down as it wouldn't be secured at all. The plate warmer is just a 120 plug.
check this short video

 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Retractable cord reel.
I've used this one in a commercial kitchen for use over a table on casters

Several problems here:

* No NRTL with online retailers like Amazon. This one says no UL.
Extension cords require testing, labeling, & listing in the united states.

* Next problem is 15A capacity is not allowed with Small Appliance Branch Circuits.
SABC's in kitchen or Laundry specifically require 20A capacity.
If originating on ceiling, it's likely a 15A circuit intended for lights, not receptacles.

* No GFCI.
SABC's specifically require GFCI protection, and possible AFCI & Tamper Resistance
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
Several problems here:

* No NRTL with online retailers like Amazon. This one says no UL.
Extension cords require testing, labeling, & listing in the united states.
It has a UL label right on it.
You can see it in the second picture 🤷
Where did you see "no UL" ?

* Next problem is 15A capacity is not allowed with Small Appliance Branch Circuits.
SABC's in kitchen or Laundry specifically require 20A capacity.
If originating on ceiling, it's likely a 15A circuit intended for lights, not receptacles.
It was a 20 amp circuit that I installed 👍

* No GFCI.
SABC's specifically require GFCI protection, and possible AFCI & Tamper Resistance
I installed a GFCI breaker 👍
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Be careful putting your work in public domains, where your peers can review it.
It has a UL label right on it.
You can see it in the second picture 🤷
Where did you see "no UL" ?
Select "User Guide" pull down, see UL = No, in Product Information section of Amazon page.

If you want Red Tag removed show us UL file number, and shipping label return address to check for internet counterfeits.
It was a 20 amp circuit that I installed 👍
If you want Red Tag removed show us a 20A product, then tell us what kind of occupancy & room?
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
Be careful putting your work in public domains, where your peers can review it.

Select "User Guide" pull down, see UL = No, in Product Information section of Amazon page.
I see a UL label on the unit. That's perfect for me 👍👍
If you want Red Tag removed show us UL file number, and shipping label return address to check for internet counterfeits.
I don't know what red tag you're talking about. This passed inspection 👍👍👍
If you want Red Tag removed show us a 20A product, then tell us what kind of occupancy & room?
Again, I don't know what red tag you're talking about. A plug-in cord isn't part of the circuit. 👍👍👍👍
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
UL is not the only listing acceptable. I put in a Level 2 Dc EV charger that was so new, that the listing company came out and did the compliance testing on site, AFTER I installed it. It was not UL, but ETL if I remember correctly. Inspector accepted it.
 