Dmc16
Member
- Location
- Sparta,nj,United states
I have a request to install a 3 phase 220 volt robot coupe (giant blender basically) in a commercial kitchen. Just confirming I understand the code correct. 150 volts to ground or less, 100 amps or less shall have gfci protection.
which would mean class a gfi since it will trip at lower leakage levels.
Even though said appliance has a twist lock, which would allow that appliance to be plugged in only to the receptacle, it is not so much what is plugged in but protecting personnel using the appliance.
Minor concern of nuisance trips with a three phase gfi bolt on breaker, unless you guys have different suggestions to protect the appliance.
thanks for the help
which would mean class a gfi since it will trip at lower leakage levels.
Even though said appliance has a twist lock, which would allow that appliance to be plugged in only to the receptacle, it is not so much what is plugged in but protecting personnel using the appliance.
Minor concern of nuisance trips with a three phase gfi bolt on breaker, unless you guys have different suggestions to protect the appliance.
thanks for the help