Commercial Kitchen GFI

Status
Not open for further replies.

dvcraven0522

Member
Location
St. Louis, Missouri
Occupation
Engineer
If say a piece of commercial kitchen equipment is hardwired (no receptacle) is this circuit still required to on a GFCI rated circuit breaker rated for personal protection?

Thank
Dan Craven
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
It will depend on the Code cycle. From 2017 to 2023 the requirements have become more restrictive.
What year Code will be enforced ??
 

kwired

Electron manager
Location
NE Nebraska
Year of code does matter. not certain of what may have changed in 2023. Dishwashers are one item common to a commercial kitchen that ended up usually requiring GFCI by 2020code even if not cord and plug connected.
 