Re: commercial kitchen sub-panel.
Froggie,
Your concern should be the connected load to the 125 amp feeder feeding the subpanel. If the connected load is low than adding a 2P-30a CB should be fine. The weakest link in your setup is the feeder, so your concern should be that the additional load won't overload the 125 amp CB.