Mr. W

Member
In a commercial kitchen there are 15 hanging duplex duplex outlets in 4" square boxes on retractable cords, must these be in a water tight box or gfci protected because actually they are not serving countertop space.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
All 15 and 20 amp 125 volt receptacles in a commerical kitchen must have GFCI protection. No exceptions.
 