I have been doing commercial kitchens since 1969. Here is what I have always done regarding disconnecting when a fire system is activated for the hood:
1) make-up air fan on hoods are disconnecetd when ANSUL fire system is activated --- exhaust fan still runs as do light.
2) the plumber has a mechanical valve in gas line to disconnect all gas appliances with ANSUL activation
3) if there are "HEAT PRODUCING" electical items under the hood I disconnect those with a shunt trip breaker activated via the ANSUL system. Like an electric fryer, electric grill, etc.
4) I do NOT disconnect general purpose receptacles that supply refrigeration power, timer power, or other non-heat generating electrical items that are under the hood.
Recently I have had 2 separate ANSIL fire protection companies tell me that under "NFPA96", NEC 2008, and "NFPA56 ?" that any outlet under the hood must be on shunt trip breakers even if its for a refrigeration. They will not tag their systems until we put all receptacles under the hood on shunt trip breakers even the ones not in use. I do NOT think this is required under any code.
I do have all GFCI's under the hood so that there is no liquid issue when the hood fire system is activated or when walls are being washed.
Can I please get some response as I do not want to install shunt trips where I do not feel they are required.
1) make-up air fan on hoods are disconnecetd when ANSUL fire system is activated --- exhaust fan still runs as do light.
2) the plumber has a mechanical valve in gas line to disconnect all gas appliances with ANSUL activation
3) if there are "HEAT PRODUCING" electical items under the hood I disconnect those with a shunt trip breaker activated via the ANSUL system. Like an electric fryer, electric grill, etc.
4) I do NOT disconnect general purpose receptacles that supply refrigeration power, timer power, or other non-heat generating electrical items that are under the hood.
Recently I have had 2 separate ANSIL fire protection companies tell me that under "NFPA96", NEC 2008, and "NFPA56 ?" that any outlet under the hood must be on shunt trip breakers even if its for a refrigeration. They will not tag their systems until we put all receptacles under the hood on shunt trip breakers even the ones not in use. I do NOT think this is required under any code.
I do have all GFCI's under the hood so that there is no liquid issue when the hood fire system is activated or when walls are being washed.
Can I please get some response as I do not want to install shunt trips where I do not feel they are required.