Commercial labeling

Status
Not open for further replies.

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
In hospitals I often seen labels on outlets. I have also seen it at other places malls etc.
Is labeling every receptacle outlet a commercial requirement?
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
Generally no. But health care may require.
Good idea as long as painters put plates back on correct receptacle
Thanks for the input I thought there was a requirement but I could not find it. Perhaps that’s why I couldn’t find it
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
517.19(A) requires receptacles from the Emergency System be identified with panel designation and circuit number.
 