I have a bid for a laundry mat and just want to make sure that I am calculating the load and advising the customer correctly. Is there anything that in the code that allows me to use a demand factor for a commercial application? I'm pretty sure that is just for a dwelling.
Combined washer name plates is 225 amps, 120 volt gas dryers combined name plate is 466 amps. Total in just washer and dryer power is 691 amps. I would think that would fall in the continuous load category. 691a x 1.25 which would be 863 amps in just washer and dryers. Then have to factor in lighting, hvac, water heater, receptacles. Just want to make sure I am right with the total amperage of 863 amps in just the laundry equipment. There is currently a 400 amp panel and a 200 amp from the old restaurant. Any one experienced in laundry mat that could give some insight. Thanks!
Combined washer name plates is 225 amps, 120 volt gas dryers combined name plate is 466 amps. Total in just washer and dryer power is 691 amps. I would think that would fall in the continuous load category. 691a x 1.25 which would be 863 amps in just washer and dryers. Then have to factor in lighting, hvac, water heater, receptacles. Just want to make sure I am right with the total amperage of 863 amps in just the laundry equipment. There is currently a 400 amp panel and a 200 amp from the old restaurant. Any one experienced in laundry mat that could give some insight. Thanks!