ryan_618
Senior Member
- Location
- Salt Lake City, Utah
I did a plan review some time ago where the engineer had specified 2.3VA per square foot for lighting in a store tyoe occupancy. I wrote on my plan review that he needed to calculate the load at 3VA per sqaure foot, in accordance with table 220.3. He replied by stating the 2.3 was adaquete.
Before I talk with him tommorrow, I want to be 100% certain that I am correct on this. There are no demand factors that can applied to the lighting load in a store, correct? Or am I losing my mind?
I want to be certain of this, as the building in question is a 95,000 square foot store, and the difference on the service/feeder load would be about 80 amps. Thanks in advance.
Before I talk with him tommorrow, I want to be 100% certain that I am correct on this. There are no demand factors that can applied to the lighting load in a store, correct? Or am I losing my mind?
I want to be certain of this, as the building in question is a 95,000 square foot store, and the difference on the service/feeder load would be about 80 amps. Thanks in advance.