mltaylor

Member
I am installing a 600 amp single phase surface for a seasonal food service building. Is it acceptable to use three residential style SqD Q0 200 amp 40 space load centers or is it necessary to use a commercial version? Naturally both exceed the possible fault current withstand rating of 14,500 volts.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
There is nothing in the NEC that would prohibit you from doing so.
 

Rewire

Senior Member
I am installing a 600 amp single phase surface for a seasonal food service building. Is it acceptable to use three residential style SqD Q0 200 amp 40 space load centers or is it necessary to use a commercial version? Naturally both exceed the possible fault current withstand rating of 14,500 volts.

Is any panel specified in the bid documents?
 