Doing a bid on a church. Is there any change in the NEC code as to placement of main breaker? Everything I've read is residential.
 
Last edited:

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
No it doesn't need to be outside. The 2020 requires an emergency disco, which can be a main panel, outside but not for non residential. Your area may have an amendment, Idk
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The panel must be adjacent to outside the church or inside as near as possible to where the service conductors enter the building.

Are you asking if the main breaker panel can have the breaker at the bottom instead of the top?
 
Location
39475
Occupation
Master Electrician
Back in 2020 the code changed on residential that the main had to be outside the home does the same rule apply to commercial buildings
 